      Buying “the biggest battery you can afford” is a common reaction to load-shedding — and often the wrong one. Size the bank from the loads you actually need during an outage, then match voltage and discharge rate to your inverter. Here is a practical way to do it for a South African home.

      Step 1 — List essential loads

      Write down each backup load in watts and how many hours you need it during a typical outage.

      Worked example (evening outage): fridge 150 W × 4 h = 600 Wh; LED lights 60 W × 4 h = 240 Wh; Wi-Fi + router 20 W × 4 h = 80 Wh; TV 100 W × 3 h = 300 Wh. Total ≈ 1,220 Wh (1.22 kWh) of useful energy. That is a modest critical-loads board — not a whole-house geyser and stove.

      Step 2 — Add usable capacity and losses

      LiFePO4 batteries are commonly used with a high depth of discharge, but you should still leave headroom. Add about 10% for inverter losses, and another buffer if you want reserve for a second outage the same day. Rule of thumb: take your Wh need, divide by 0.9 (losses), then add 20–30% reserve for comfort.

      From the example: 1.22 kWh ÷ 0.9 ≈ 1.36 kWh; with 30% reserve ≈ 1.8 kWh usable. A single 5 kWh module is already more than enough for that critical set — which is why many homes start at 5 kWh and grow later.

      Step 3 — Match battery voltage to the inverter

      • 48V / 51.2V LV: the usual home hybrid pairing.
      • High-voltage stacks: only with HV hybrid / PCS inverters. Never force an LV battery onto an HV inverter.

      Confirm CAN/RS485 compatibility on both product pages before you order.

      Step 4 — Check C-rate and peak current

      A kettle (~2,000 W), microwave or geyser element can trip a small inverter or pull more current than a small battery bank should deliver continuously. Size the inverter for surge and continuous power, and make sure the battery’s allowed discharge current covers those peaks. If a load is optional during outages, leave it off the backup board.

      Illustrative sizes (not a guarantee)

      Bank size Typical critical-load use
      ≈5 kWh Fridge, lights, Wi-Fi, laptops/TV for several hours; manage kettle use
      ≈10 kWh Same plus longer outages or a few heavier intermittent loads
      ≈15 kWh+ Larger homes, partial air-con/geyser backup, or multiple cycles per day

      These are planning guides. Your installer should calculate from your actual load list and inverter limits.

      Shop batteries and cabling

      See lithium batteries, Dyness batteries, high-voltage batteries, and cables & connectors. All store prices are VAT-inclusive. Ask Powerforum if you want a second opinion on sizing.

      FAQ

      Is 5 kWh enough for stage 6?

      It can be — if the backup board is limited to essentials. Whole-house backup through long stages usually needs more capacity and a larger inverter.

      Can I add modules later?

      Many LiFePO4 ranges allow parallel expansion within brand/model rules. Check the maximum parallel count and whether new and old modules should be the same batch/firmware.